News: Anyone wishing to register as a new member on the forum is strongly recommended to use a "proper" email address - following recent spam/hack attempts on the forum, all security is set to "high", and "disposable" email addresses like Gmail, Yahoo and Hotmail tend to be viewed with suspicion, and the application rejected if there is any doubt whatsoever
 
Recent Articles: Navitron Partners With Solax to Help Create A More Sustainable Future | Navitron Calls for Increased Carbon Footprint Reduction In Light of Earth Overshoot Day | A plea from The David School - Issue 18
   Home   Help Search Login Register  
Pages: [1] 2   Go Down
  Print  
Author Topic: New build eco-house solar pv and battery sizing  (Read 5236 times)
dan_b
Hero Member
*****
Online Online

Posts: 4254


WWW
« on: July 08, 2019, 08:18:44 AM »

Hi chaps
I have a friend who is in the process of designing a new build which he wants to be as eco as possible - they're going for passiv-haus levels of insulation and heating demand, but the bit they're now trying to work out is the size of the solar and battery they should look to install.

Roof size wise with modern 400W panels he could probably get 16kW of panels on a south-facing roof.  But there must come a point where there's really no value in putting extra panels on and spending more money on storage or other self-consumption devices, and of course there's no FiT payment anymore?

I have said to him to consider perhaps a smaller south-facing array but then to add some west-facing panels to extend the evening generation profile, but basically - for those of you here who are effectively zero-import on electricity, or actually fully off-grid,  what sort of sized PV and battery array are you looking at as a rough rule of thumb?

They'll get a decent sized battery system like a Tesla PowerWall, and they're looking at the SunAmp heat batteries for hot water storage plus occasional heating requirements.   But they're intending not to have a gas connection at all, so cooking would be electric.  They're looking at a  heat pump for occasional heating requirements in the winter.

Is it really as simple as "fit as much solar as you can", or is there a point where there's really no point adding any more, and indeed you'd be better off spending on extra batteries?

Any thoughts/ suggestions?
Logged

3.06kWp SolarEdge system with a split array:
2.18kWp 10x South facing, plus 4x West facing 880W

Mk1 ImmerSUN DHW diverter
4kW PowerVault Battery

Tesla Model 3 Long Range
Fintray
Hero Member
*****
Offline Offline

Posts: 817



« Reply #1 on: July 08, 2019, 10:26:57 AM »

Dan

I've 14kWp of PV (3.87 which gets FIT's) and a Powerwall 2 battery and in the last 3 months have imported about 6kWh from the grid, A PV diverter has supplied all my hot water and extra power has been used to supply heating when required. There is also the option of going for the Outgoing Octopus tariff from Octopus Energy which gives a flat rate 5.5p/kWh or a variable rate if you go Agile.


So if your friends have passiv-haus levels of insulation their heating requirements should be pretty minimal and if they go for A++ rated appliances their electricity requirements could be very reasonable meaning more to export if they can get approval for that level of export, failing that they could install SolarEdge inverters and limit their export.
Logged

3.87kWp PV
10.24kWp PV SolarEdge system
Tesla Powerwall 2
100 x 47mm Navitron tubes (still being installed!)
MK2 PV router DHW diverter
Morso 5kW WBS
Nissan Leaf
A.L.
Hero Member
*****
Offline Offline

Posts: 908


« Reply #2 on: July 08, 2019, 04:26:01 PM »

hello,

- I would limit it to an annual output 2x their current/likely annual appliance use. The summer excess can heat the hot water initially with an EV in short order to soak up the rest, maintain their eco-credentials. After all it will always be possible to add more later (although that will be subject to VAT). As for batteries, 4 usable days storage should be the max.
Logged
brackwell
Hero Member
*****
Online Online

Posts: 3060


« Reply #3 on: July 08, 2019, 07:12:56 PM »

I think a lot of this depends on where you live,no.of people, no/mileage of EVs. and other large personal loads

I live on the south coast and if i was building paasivhaus standard i would not have a heating system relying on passiv solar, and a pellet stove and/or leccy storage heaters (on E7) for just in case.

Ken

Logged
nowty
Hero Member
*****
Offline Offline

Posts: 804



« Reply #4 on: July 09, 2019, 04:56:47 PM »

Solar PV is so cheap now that I would "fit as much solar as you can" as you will never have enough in winter, you will wish you had more in Spring / Autumn and you can always sell excess back to the grid in summer. This is especially so if your friend is going for a Powerwall as this will help soak up the excess generation.
Logged

11kW+ of PV installed and 56+ MWh generated.
Lithium battery storage of 50+ kWh.
Hot water storage of 15+ kWh.
Heat storage of 15+ kWh.
6kW Ground source heatpump.
EV BMW i3 (another 30+ kWh's of storage).
260,000+ litres of water harvested from underground river.
Home grown Fruit and Veg.
dan_b
Hero Member
*****
Online Online

Posts: 4254


WWW
« Reply #5 on: July 09, 2019, 06:16:17 PM »

Thanks thatís basically what I thought - I have suggested he might want to try and pop some West facing panels in to stretch the generation profile out a bit.
With panels now routinely in the 300+ watts rating does anyone care about panel efficiency anymore or is it really just down to get as much kWp as you can for the lowest acquisition cost?
Logged

3.06kWp SolarEdge system with a split array:
2.18kWp 10x South facing, plus 4x West facing 880W

Mk1 ImmerSUN DHW diverter
4kW PowerVault Battery

Tesla Model 3 Long Range
Iain
Hero Member
*****
Offline Offline

Posts: 1727


« Reply #6 on: July 09, 2019, 06:26:57 PM »

Hi

Quote
I have suggested he might want to try and pop some West facing panels in to stretch the generation profile out a bit.

Possibly less important with a battery as the battery will "Stretch the profile"

Iain
Logged

1.98kWp PV (11 x Sharp 180 and SB 2.5)
20 x 65mm Thermal and 180ltr unvented
Powervault 4Kw - G200 Lithium-Ion (LiFePO4)
9000ltr rainwater storage   Plymouth
billi
Global Moderator
Hero Member
*****
Offline Offline

Posts: 8945



WWW
« Reply #7 on: July 09, 2019, 06:43:53 PM »

Exactly as Iain said , if the  array is on the south facing roof then  at that size it will still deliver   some   at  the morning and evening  ( when  the kettle is on  for coffee in morning or the pizza oven  in the evening )

Maybe me sentimental , it hurt me to   have the  el. oven on in the evening  and too much power came from the battery  .... but  i have  only 4 kW PV

the tesla  power wall  is far too small and far too expensive  , a 100 kWh   industrial fork lift battery similar price ,  will suit a 10 -15 kw PV much better  , for  beside electricity , for heating , hot water and electric driving

a 15 kW PV is doing about 20 kWh on average a day in November  in South UK  , so ....



Billi


« Last Edit: July 09, 2019, 06:48:53 PM by billi » Logged

1.6 kw and 2.4 kw   PV array  , Outback MX 60 and FM80 charge controller  ,24 volt 1600 AH Battery ,6 Kw Victron inverter charger, 1.1 kw high head hydro turbine as a back up generator , 5 kw woodburner, 36 solar tubes with 360 l water tank, 1.6 kw  windturbine
Scruff
Hero Member
*****
Offline Offline

Posts: 1232



« Reply #8 on: July 09, 2019, 07:15:34 PM »

What are the benefits of a battery for a grid connected installation?
Logged
billi
Global Moderator
Hero Member
*****
Offline Offline

Posts: 8945



WWW
« Reply #9 on: July 09, 2019, 07:20:04 PM »

well what are the benefits of  a big PV then in times of no FiT ?
Logged

1.6 kw and 2.4 kw   PV array  , Outback MX 60 and FM80 charge controller  ,24 volt 1600 AH Battery ,6 Kw Victron inverter charger, 1.1 kw high head hydro turbine as a back up generator , 5 kw woodburner, 36 solar tubes with 360 l water tank, 1.6 kw  windturbine
nowty
Hero Member
*****
Offline Offline

Posts: 804



« Reply #10 on: July 09, 2019, 07:23:58 PM »

Hi

Quote
I have suggested he might want to try and pop some West facing panels in to stretch the generation profile out a bit.

Possibly less important with a battery as the battery will "Stretch the profile"

Iain

I agree that if you have a small PV array, then a battery will stretch the profile, thus better to have it all facing south, but I find that if you have a large array it helps reduce the peak power generation problem if you spread it around and its more efficient to use the power as its generated rarther than store it in batteries.

My last lot of PV has gone on my NE facing roof. Partly cos there is no more room elsewhere for it !, but also because it helps me run my heatpump from very early in the morning (Mar to Sep) without solely relying on the batteries.
« Last Edit: July 09, 2019, 10:42:26 PM by nowty » Logged

11kW+ of PV installed and 56+ MWh generated.
Lithium battery storage of 50+ kWh.
Hot water storage of 15+ kWh.
Heat storage of 15+ kWh.
6kW Ground source heatpump.
EV BMW i3 (another 30+ kWh's of storage).
260,000+ litres of water harvested from underground river.
Home grown Fruit and Veg.
Scruff
Hero Member
*****
Offline Offline

Posts: 1232



« Reply #11 on: July 10, 2019, 12:33:39 AM »

well what are the benefits of  a big PV then in times of no FiT ?

Competitive cost-effective power.

A battery is an efficiency reduction device of arguable financial merit. Data to prove otherwise from existing installations is not something I've witnessed. I'd love to see some. 
Can it compete with cables and direct drive? Why does it compete with cables and direct drive?
Looks like an expensive endeavor in proprietary electron farming.

Genset offsetting is an entirely different fish of kettles.
Logged
billi
Global Moderator
Hero Member
*****
Offline Offline

Posts: 8945



WWW
« Reply #12 on: July 10, 2019, 06:48:40 AM »

Scruff , there is a other point too in my opinion

While there was a war in Irak   and the the german government decided at the time to send  soldiers there , there was a movement of  people  called "no blood for oil"   many business people of that movement refused  to pay their tax  at those years

If anyone   refuse to   connect to the grid  and tries not  to joining criminal politics , like it is happening in the the UK and Germany right now , with  minor or close to nil  incentives  towards a faster  conversion towards a fossil-fuel  free politics  , then   i am still convinced to  advice people to cut the line and do not  wait .

That was my decision  15 years back  to not connect to the Irish Grid

So being off grid is more viable and cost efficient nowadays  then ever ,  sure  it needs  a situation that suits   and some investment upfront ( that does not mean its more expensive then  a grid  connected idea )  , but with those factors of electricity ,  heat  and hot water ,  electric charging  one can  utilize  own sun power pretty   good  and  with a sunny smile

Billi
Logged

1.6 kw and 2.4 kw   PV array  , Outback MX 60 and FM80 charge controller  ,24 volt 1600 AH Battery ,6 Kw Victron inverter charger, 1.1 kw high head hydro turbine as a back up generator , 5 kw woodburner, 36 solar tubes with 360 l water tank, 1.6 kw  windturbine
dan_b
Hero Member
*****
Online Online

Posts: 4254


WWW
« Reply #13 on: July 10, 2019, 09:15:22 AM »

Right so to summarise the advice here is now
Big arrays are pointless
Storage is pointless
Going off grid is the only solution
But only if you have a big array and a big battery?
Logged

3.06kWp SolarEdge system with a split array:
2.18kWp 10x South facing, plus 4x West facing 880W

Mk1 ImmerSUN DHW diverter
4kW PowerVault Battery

Tesla Model 3 Long Range
knighty
Hero Member
*****
Offline Offline

Posts: 2798


« Reply #14 on: July 10, 2019, 10:34:51 AM »

I'd go for as much PV as possible... but as you said split some onto the other side of the roof... maybe keep most of it south facing?

do you know what his export limit is? - it could be an option to miss out the battery for now and cover both roovs in PV, probably more cost effective (with 5p/kwh for export)

then... if he wants batteries add them later when they're cheaper?  (prices are falling pretty quick?)
Logged