News: Anyone wishing to register as a new member on the forum is strongly recommended to use a "proper" email address - following recent spam/hack attempts on the forum, all security is set to "high", and "disposable" email addresses like Gmail, Yahoo and Hotmail tend to be viewed with suspicion, and the application rejected if there is any doubt whatsoever
 
Recent Articles: Navitron Partners With Solax to Help Create A More Sustainable Future | Navitron Calls for Increased Carbon Footprint Reduction In Light of Earth Overshoot Day | A plea from The David School - Issue 18
   Home   Help Search Login Register  
Pages: [1]   Go Down
  Print  
Author Topic: Buffer tank fill levels?  (Read 363 times)
chris wills
Full Member
***
Offline Offline

Posts: 138


« on: November 09, 2019, 11:40:41 AM »

Just wandering how full should my buffer tank be for my ASHP?
As I have had some maintenance done over the past few weeks and lost some of it probably, should it be full to the top or something else?


It's a 200 litre cylinder, should it be full to the top?
« Last Edit: November 09, 2019, 02:02:54 PM by chris wills » Logged
benseb
Newbie
*
Offline Offline

Posts: 45


« Reply #1 on: November 09, 2019, 04:36:43 PM »

Should be completely full with any air bled from the top.
Logged
chris wills
Full Member
***
Offline Offline

Posts: 138


« Reply #2 on: November 09, 2019, 05:14:12 PM »

That makes sense, I'll top it up
Logged
Nickel2
Hero Member
*****
Offline Offline

Posts: 1730


Method mixed with Madness


« Reply #3 on: November 10, 2019, 09:15:43 AM »

Remembering to take expansion into account...
Logged

1.140kW mono south-facing at 49*
EpEver 4210A at 24v
24V 400 Ah battery. (4x200Ah FLA)
EpEver STI1000-24-230 pure sine inverter
Of course it'll work. (It hasn't caught fire yet).
chris wills
Full Member
***
Offline Offline

Posts: 138


« Reply #4 on: November 10, 2019, 10:31:46 AM »

I have an expansion vessel in line.
Any advice?
Logged
rogeriko
Hero Member
*****
Offline Offline

Posts: 1409



WWW
« Reply #5 on: November 10, 2019, 09:09:47 PM »

Thats a pressurised system buffer. It should have a good 1.5 bar pressure in it. I suggest you call a plumber who can work on pressurised systems and get him to check it out before something expensive gets damaged.
Logged

chris wills
Full Member
***
Offline Offline

Posts: 138


« Reply #6 on: November 11, 2019, 12:42:05 PM »

should I top up when all the rads are open so the water is flowing into them, to see how much the tank needs to be topped up by?
I don't think there is enough coolant in the system.
The ASHP comes on every 15-20 mins, is that normal?
Logged
JohnS
Hero Member
*****
Offline Offline

Posts: 2020


« Reply #7 on: November 11, 2019, 08:27:57 PM »

Top up the pressure
Bleed the radiators
Top up again
Repeat as necessary

Best to do it with the system off.  Not sure if that is to prevent the risk of scalding water squirting out or of sucking air in if the pump is installed on the return side and thus could be more suction than push.  But generally recommended.
Logged