News: Anyone wishing to register as a new member on the forum is strongly recommended to use a "proper" email address. Following continuous spam/hack attempts on the forum, "disposable" email addresses like Gmail, Yahoo and Hotmail tend to be viewed with suspicion, and the application rejected if there is any doubt whatsoever
 
Recent Articles: Navitron Partners With Solax to Help Create A More Sustainable Future | Navitron Calls for Increased Carbon Footprint Reduction In Light of Earth Overshoot Day | A plea from The David School - Issue 18
   Home   Help Search Login Register  
Pages: [1] 2   Go Down
  Print  
Author Topic: Cheap inverter repair  (Read 1283 times)
ecogeorge
Hero Member
*****
Offline Offline

Posts: 1439

Forest of Dean -Gloucestershire


« on: March 30, 2020, 08:18:25 PM »

My cheap chinese grid tie inverter has just stopped working. I did have a poor joint on a Mc4 connector that may be related .
Has not been subject to over voltage , fuse is good, on/off switch works.
Anyone got any pointers ?? every component looks good, no burnt triacs ,no burst capacitors , no smell of magic smoke .....
George



Logged
RIT
Hero Member
*****
Offline Offline

Posts: 2317

South West London


« Reply #1 on: March 30, 2020, 09:49:05 PM »

Any fault finding would most likely involve powering the unit up unless it was a very simple where a single part had failed, Which would mean high voltages all over the place and so not somewhere you want to go fault finding without a good understanding of what you are doing. Even a simple part fault needs more than a standard multi-meter unless its a resistor or diode.

What can you tell us about the device - a number of posters here have shown that they are good at tracking down hints and tips from the outer reaches of the web.
Logged

2.4kW PV system, output can be seen at  - https://pvoutput.org/list.jsp?userid=49083

Join the fight against human malware at https://stats.foldingathome.org/team/259956

Why bother? - well, there is no planet B
ecogeorge
Hero Member
*****
Offline Offline

Posts: 1439

Forest of Dean -Gloucestershire


« Reply #2 on: March 31, 2020, 03:39:50 PM »

All i can tell you is its a model no.GP_350w  DC 28-52v   220ac output. Maybe better pics here .......





George
Logged
RIT
Hero Member
*****
Offline Offline

Posts: 2317

South West London


« Reply #3 on: March 31, 2020, 04:55:41 PM »

I just had a look around and the only fault repair I could find was a video in Italian, so no real help apart from the fact that they replaced one of the MOSFETs which are the devices that line the sides of the board and use the case as a large heat sink.

I also found that there is a UK seller on eBay at £40. If that is the going rate for these devices now it would not make much sense to pay someone to fault find your current unit.

    https://www.ebay.ie/itm/323488002673
Logged

2.4kW PV system, output can be seen at  - https://pvoutput.org/list.jsp?userid=49083

Join the fight against human malware at https://stats.foldingathome.org/team/259956

Why bother? - well, there is no planet B
Nickel2
Hero Member
*****
Offline Offline

Posts: 1868


Sunny North-East Hampshire


« Reply #4 on: March 31, 2020, 07:11:29 PM »

I paid £30 for a similar job that worked for 18 months, then the pcb broke down and it arced itself to death. New MOSFETs cost more than the original thing, so now it's in the spare-parts box for use in another project.
Logged

1.140kW mono south-facing at 49*
EpEver 4210A at 24v
New (Old) 8S7P LiFe battery, 105Ah @ 26.4V
EpEver STI1000-24-230 pure sine inverter
Of course it'll work. (It hasn't caught fire yet).
ecogeorge
Hero Member
*****
Offline Offline

Posts: 1439

Forest of Dean -Gloucestershire


« Reply #5 on: March 31, 2020, 07:46:27 PM »

Working from home has resulted in a few  online videos .....
I can confirm the mains fuse is good.
All mosfets test at 3.3k ohms which indicates good.
Next step is to power up on bench (cafefully) and have a probe .......
George
Logged
rogeriko
Hero Member
*****
Offline Offline

Posts: 1443



WWW
« Reply #6 on: March 31, 2020, 08:00:53 PM »

The black item in the middle marked BLX is a fuse holder. Is that the fuse you have checked?
Logged

TT
Sr. Member
****
Offline Offline

Posts: 318


« Reply #7 on: March 31, 2020, 08:39:12 PM »

Rogeriko to the rescue again- ( he helped when I was trying to repair mine) good shout

Whatís the white component to the right of this blx fuseholder?
Could it be a varistor?
Logged
ecogeorge
Hero Member
*****
Offline Offline

Posts: 1439

Forest of Dean -Gloucestershire


« Reply #8 on: March 31, 2020, 09:18:59 PM »

Yes ,blx fuse is good and so is holder -tested on back of pcb.
If i remember the inverter is completely dead ,-no lights at all - DC voltage is reduced when pv connected.
Have a 35v transformer  -need to find a rectifier to make text supply.
George
Logged
rogeriko
Hero Member
*****
Offline Offline

Posts: 1443



WWW
« Reply #9 on: March 31, 2020, 09:29:38 PM »

Put a rectifier and then an electrolytic capacitor. This will give you about 45 volts DC. Then you must put a current limiting light bulb in series with the dc line to the inverter. This will limit the current to 1 amp or so otherwise you will immeadiately burn out your transformer. Start off with a 100w light bulb. If it glows slightly then you have a shorted transistor. Likely.          I test big inverters like this only using a 240/240 transformer.       Dangerous.
Logged

Nickel2
Hero Member
*****
Offline Offline

Posts: 1868


Sunny North-East Hampshire


« Reply #10 on: April 01, 2020, 10:40:00 AM »

...'Whatís the white component to the right of this blx fuseholder?'...
It looks like a GDT (Miniature Gas Discharge Tube) used as a protection device to catch high-voltage spikes.
They are used in telephone exchanges on the line-side to protect against static voltages. (lightning).
Used with a fuse, they go short when they strike, blowing the fuse and isolating the equipment.
They also serve to protect anyone working on the equipment.
Logged

1.140kW mono south-facing at 49*
EpEver 4210A at 24v
New (Old) 8S7P LiFe battery, 105Ah @ 26.4V
EpEver STI1000-24-230 pure sine inverter
Of course it'll work. (It hasn't caught fire yet).
TT
Sr. Member
****
Offline Offline

Posts: 318


« Reply #11 on: April 01, 2020, 05:11:47 PM »

Hi Rogeriko,

Can you provide more info on the testing with a series lamp as a current limiting device, havenít heard that and interested in it myself.

Thanks!
Logged
Tinbum
Hero Member
*****
Offline Offline

Posts: 1224


« Reply #12 on: April 01, 2020, 07:57:48 PM »

The bulb is in effect just a resistor. If the item being tested has a short then the the current will be limited by the bulb- ie it tries to light. You don't have a dead short with a large current.
Logged

85no 58mm solar thermal tubes, 28.5Kw PV, 3 x Sunny Backup 5048, 3x Sunny Island 5048, 2795 Ah (135kWh) (c20) Rolls batteries 48v, Atmos wood gasification boiler, Brosley wood burner, 2000lt buffer tank and 250lt DHW
jonesy
Hero Member
*****
Offline Offline

Posts: 846



« Reply #13 on: April 01, 2020, 08:35:40 PM »

I've had the transformer come adrift, breaking the fine copper primary.
Does the other side of the pcb have the control electronics? No stray nut shorting it out.
If it's completely dead, try to identify the dc-dc converter from 50v to 5v(or 3.3v) that will probably start with just the battery connected - my sma gti lights up and starts communicating with just the panels.
Logged

1.1kWp PV & SB1700. 7kW log burner.
rogeriko
Hero Member
*****
Offline Offline

Posts: 1443



WWW
« Reply #14 on: April 01, 2020, 09:20:53 PM »

Tinbum is right. The lamp is just a resistor that you can see. Large inverters have big capacitor banks that are like a dead short when you first apply dc power. The lamp will come on bright as the capacitors charge, then as the charging current drops the lamp goes out. In this case with a probable shorted transistor the lamp will remain lit because there is a short. A grid tie inverter will start feeding into the mains and as the power ramps up the lamp will get brighter, then you must disconnect the dc power quick before the magic smoke gets released from your transformer, but at least you know the GTI works.
Logged